Question
How can I monitor sensors
Offline

I have a poseidon 3268 and I wanna monitor and make alarms for its sensor, but I couldn't do it. I would appreciate if you please help me to find a way.
-----
- 657 views
- 1 version
- 32 replies
- 4 followers
- Post Date:
- May 1, 2012
- Posted By:
- zahra adeli
About this forum
- 143k views
- 2224 topics
- 55 followers
Post questions and find answers for all things related to the Standard and Premium Editions of WhatsUp gold.
Viewed 657 times
Page Options
32 Replies
you have to enable SNMP and get the required MIB file
Poseidon family SNMP OID description
-----------------------------------------------------------------------------------
Poseidon Device Values:
-------------------------------------------------------
.1.3.6.1.2.1.1.1.0 Device description (string)
.1.3.6.1.2.1.1.5.0 Device name (string)
Dry Contact Inputs
-------------------------------------------------------
.1.3.6.1.4.1.21796.3.3.1.1.2.1 Contact Input 1 state (integer, 1=Off, 2=On)
.1.3.6.1.4.1.21796.3.3.1.1.2.3 Contact Input 3 state (integer, 1=Off, 2=On)
.1.3.6.1.4.1.21796.3.3.1.1.3.1 Dry Contact Input 1 name (R/W string)
.1.3.6.1.4.1.21796.3.3.1.1.4.1 Dry Contact Input 1 Alarm state (integer)
Sensor
-------------------------------------------------------
.1.3.6.1.4.1.21796.3.3.3.1.6.1 Sensor 1 current value *10 (integer)
.1.3.6.1.4.1.21796.3.3.3.1.6.2 Sensor 2 current value *10 (integer)
.1.3.6.1.4.1.21796.3.3.3.1.6.10 Sensor 10 current value *10 (integer)
.1.3.6.1.4.1.21796.3.3.3.1.2.1 Sensor 1 name (R/W string)
.1.3.6.1.4.1.21796.3.3.3.1.2.2 Sensor 2 name (R/W string)
.1.3.6.1.4.1.21796.3.3.3.1.4.1 Sensor 1 state (integer, 0=Invalid, 1=Normal, 2=AlarmState, 3=Alarm)
.1.3.6.1.4.1.21796.3.3.3.1.5.1 Sensor 1 current value, units included (string)
.1.3.6.1.4.1.21796.3.3.3.1.8.1 Sensor 1 unique ID (integer)
.1.3.6.1.4.1.21796.3.3.3.1.9.1 Sensor 1 units (integer, 0=°C, 1=°F, 2=°K, 3=%, 4=V, 5=mA, 6=unknown, 7=pulse, 8=switch)
Outputs
-------------------------------------------------------
.1.3.6.1.4.1.21796.3.3.2.1.2.1 Output 1 state (R/W integer, 1=Off, 2=On)
.1.3.6.1.4.1.21796.3.3.2.1.2.2 Output 2 state (R/W integer, 1=Off, 2=On)
.1.3.6.1.4.1.21796.3.3.2.1.3.1 Output 1 name (R/W string)
For more details, analyze MIB file or Cheb detailed device's manual..
Dear Zahra, this device support SNMP.
You can find the MIB here: http://www.hw-group.com/download/fw/pos3268/Poseidon_3268.mib
More information needed? http://www.hw-group.com/software/pd_utils_en.html
Thanks so much, I have the OID description, but the problem is that when I wanna fill the the relevant blank field in monitoring page, the field is not active and i cannot enter the OID, I worked with OPManager bit I found it's alarm notification so poor, so I choose WUG, but it didn't work.
I go to Admin Tab, then performance monitoring, what about after? I would appreciate if you please explain it to me step by step
You can create a new Performance Monitor http://docs.ipswitch.com/NM/79_WhatsUp%20Gold%20v15/03_Help/index.htm?29226.htm?zoom_highlight=performance+monitot?toc.htm
Then you should select SNMP Performance Monitor
Thank you so much, the problem is that I read those parts several times and create custome monitor, with the relevant OID, but nothing happens, I mean no result of monitoring, no graph, nothing is available.
what can I do with that?
Dear Detlef
I have the MIB file for poseidon, I didn't use it before, when I was working with OPmanager there was no need to work with MIB file, I don't what is actually and how does it work.
Thanks for your answers
@Zahra - you don't need the MIB file to monitor the device. Once you have configured the monitor, you need to make sure that you apply it to the devices that you wish to monitor.
Dear Jason
I apply the configuration to the device, but no result I have, I don't know what to do. when I go to custom monitor tab, no curve, no data is available
what is the "instance" on monitoring library? should it be a particular nember?
This is the message that I have in the "performance monitor log"
Response packet contained the error: No Such name
What should I do?
That error message typically means wrong community string. I would recommend using the SNMP MIB Walker tool to verify that you can successfully communicate with the target device via SNMP, before you go any further with the monitor.
Dear Jason,
I set the credential in my device and choose a same name for both of community even in device and WUG, but nothing happened, WUG knows my device and when I check the status with the Ping command, everything is ok.
so what now? is there any other solution for this problem?
Thanks so much for your attention
Ping requests don't require SNMP credentials, so it doesn't surprise me that Ping checks work. I am confident that the issue here is with the SNMP configuration on the target machine. Again, please try using the SNMP MIB Walker tool to attempt communicating with the target device using SNMP. If that doesn't work, you will need to verify the configuration of SNMP on that machine.
Dear Jason,
It worked finally, Now I have some custome performance monitor curves, thanks many.
In the next step I started to define threshold for my monitors, according to user guide everything is ok but there is no alarm or report when the value exceeded the threshold value,
I'm sure it's because of my misunderstanding about the steps for configuration,
I read it several times but no result I got,
what should I do now?
Thank you for your kind help
My question is that how can I assign an action to a monitor performance?
if you are talking about Alert Center, you can edit the required Threshold and add the required Notification Policy (Email and SMS Direct actions only).
Attachments
Dear Ahmed I configured threshold library and define threshold for my monitors, but when the value goes beyond deined limit, no report is created. I want to creat reports and alarms when this happens.
can you please check the time of Threshould
for example: Disk Utilization exceeds XX% for 30 Min
can you use a samll time period, just for test??
Dear Ahmed
my custome monitor is temperature and it's always aound 30 C, I define the time 10 minutes and 20 for threshold. is it correct that in threshold dialoge I select global monitor and from select device tab I choose my poseidon? if this is correct I don't know what else I can do
can you please send a screenshot from the Threshold created
Dear Ahmed
Here is the screenshot
Attachments
Did you assign this Custom Performance monitor to the corresponding device?
Dear Ahmed,
can we have a conversation with gtalk or something else?
in select device tab< I choos poseidon 3268
yes I assign it to device
Attachments
I think that you are choosing the wrong monitors...
Can you check the monitors from upper part in Performance monitors and untick the lower part monitors...
Or
keeping all device settings as the same and choose Device Specific Monitors from your threshold
I did what you said, from where I can see the result?
I went to Home->Top10 and add costume monitore, but when I wanna configure this window, an error dialoge box which says:
Server Error in '/NmConsole' Application.
Runtime Error
Description: An application error occurred on the server. The current custom error settings for this application prevent the details of the application error from being viewed.
I saw a message on device page, it worked what u suggest. Thanks many. so if I wanna have several monitors and threshold, what should I do?
and another question : can I define a sound alarm for this threshold violation? I went to action library and define some sound action, then go to the device page and assign this new action to the device, but in a change state dialoge box, which one I must choose?
Hi Zahra,
You have 2 ways to configure Custom Performance Monitors
kindly find the attached file
From your screenshot, I find the following:
Attachments
Dear Ahmed
Thank you for the attached file, very helpful it was. I finally could creat some report on threshold violation.
Now if I wanna define alarm sound or another action for this situation, what shuold I do? I used action library and created some action, when I wanted to assign this to my device, it was just on down or up status of my device that this action would perform, what if I want the sound on my threshold violation?
Thanks again
Alert Center uses onlySMS Direct and Email Actions.